Trickle Charge - A charge at a low rate, balancing losses through local action and/or periodic discharge, to maintain a cell or battery in a fully charged condition.
Output (rated) - Apparent power Pn that the UPS can deliver under given load conditions (power factor = 0.8).
Circuit breaker (battery) - DC circuit breaker that protects the battery of a UPS.(back)
Closed-Circuit Voltage (CCV) - The potential or voltage of a battery when it is discharging or charging.
Inverter (off-line or stand-by) - UPS configuration in which the inverter is parallel-mounted to the load supply line and backs up the mains. This configuration offers a substantial cost reduction but is applicable only to low outputs, under 3 kVA, because it results in an interruption lasting up to 10 ms during transfer and does not filter inrush currents.
Cutoff Voltage (also see End Voltage) - The battery voltage at which the discharge is terminated. The cutoff voltage is specified by the battery manufacturer and is generally a function of discharge rate.
Earthing system TN - Earthing system in which the exposed conductive parts are interconnected and connected to the neutral. The neutral is connected to the earth. The installation must be de-energized immediately in the event of an insulation fault.